how many 14-2 per a 4"(w)*4"(l)*2"(D) box?

Thanks.. I searched and couldnt find the calculation
 
  #2  
Old 12-26-03, 04:27 PM
hornetd's Avatar
Member
Join Date: Aug 2001
Location: Maryland
Posts: 695
Received 0 Votes on 0 Posts
The box you describe is not a standard box. If you meant a four inch square by 2&1/8" deep box it has a nominal internal volume of 30.3 cubic inches. Since each number #14 AWG conductor needs a 2 cubic inch space it can hold 15 #14 AWG conductors. If the clamps are external and there are no devices or hardware in the box it can hold seven 14/2 w/ground cables. All of the equipment grounding conductors only count as one conductor.
--
Tom
 
  #3  
Old 12-26-03, 04:43 PM
C
Member
Thread Starter
Join Date: Apr 2002
Location: USA
Posts: 220
Received 0 Votes on 0 Posts
THANKS. it must be 2 1/8" . just took a quick measurement!
 
  #4  
Old 12-26-03, 07:29 PM
ERIKGENE's Avatar
Member
Join Date: Mar 2003
Location: NEW YORK - PUTNAM COUNTY
Posts: 109
Received 0 Votes on 0 Posts
FYI: some of the plastic boxes also list the wire capacity imprinted on the inside, unless you look closely you can miss it.
 
 