Electrical Outlet rating question

Reply

  #1  
Old 12-29-03, 12:53 PM
rocketir
Visiting Guest
Posts: n/a
Electrical Outlet rating question

Just bought an older house. Around 35 yrs old. 100 amps service panel with 20 amp breakers with 12/3, 12/2 Cu wire. When I would plug stuff into my outlets alot of the times the plug would fall out. I figured that the outlets were old and worn. So I replaced all the outlets in the house with new ones. Took a good look at one today and noticed that I had replaced them all with 15 amp outlets. Now the breakers are still 20 amp breakers. Am I going to run into a problem later on? Not sure about the rating of the original outlets as I have tossed them all. But physically they look the same. They did not have the extra prong on them.
 
Sponsored Links
  #2  
Old 12-29-03, 01:03 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
It's fine. Code allows 15-amp switches and receptacles on a 20-amp circuit.

I'm not sure if this is an issue with you, but it is not legal to install receptacles with a grounding hole if the receptacle is neither grounded nor GFCI protected. This may not be an issue since you seemed to imply that you had a grounding source at each box.
 
  #3  
Old 12-29-03, 02:02 PM
rocketir
Visiting Guest
Posts: n/a
Thanks for the response. Yes I did ground each recepticle. What I was trying to say was that the old ones didn't have one plug turned horizontal.
 
  #4  
Old 12-29-03, 03:59 PM
ERIKGENE's Avatar
Member
Join Date: Mar 2003
Location: NEW YORK - PUTNAM COUNTY
Posts: 109
Received 0 Votes on 0 Posts
Not sure on this John, but should'nt the outlets be pig-tailed ?
Since the circuit and wire is 20amp, your relying on the bar from a 15 amp recepticale to carry through your current ? What happens when you pull more than 15, but less than 20 from the outlets.
 
  #5  
Old 12-29-03, 04:02 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
All 15-amp receptacles that are UL approved are designed and tested for 20-amp pass-through current.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: