NM Cable in Conduit?


  #1  
Old 01-28-04, 08:27 PM
bdek
Visiting Guest
Posts: n/a
Question NM Cable in Conduit?

Can I use NM (Romex 12/2 w/ grnd. or 12/3 w/ grnd. ) cable in 1/2" EMT?

The conduit would protect a NM cable drop from approximately 6" below a wooden residential floor joist to an outlet box on a concrete block basement wall at about 48" above the floor. Would I still remain within the NEC conduit fill requirement using the above cables?

This technique seems to simplify the overall installation.

Comments appreciated,
Thanks,
Bob
 
  #2  
Old 01-28-04, 11:34 PM
green jacket's Avatar
Member
Join Date: Sep 2000
Location: Williamsport and Blue Bell, Pennsylvania
Posts: 489
Upvotes: 0
Received 0 Upvotes on 0 Posts
Your installtion will be code compliant by leaving the jacket on the romex down to the EMT connetor on the box, and having an adapter that has a romex connector on one side and EMT connector on the other side. An alternative is to use a regular romex connector, reg. EMT connector, and thread them into a rigid coupling of the correct size. Be sure to put a grounding screw in the box, and bond it.

The plan you have is good, I commonly install surface mounted basement receptacles in EMT, and need to convert to and from romex periodically for a homerun or lighting run.

good luck,

gj
 
  #3  
Old 01-29-04, 09:10 AM
bdek
Visiting Guest
Posts: n/a
Thanks gj.

I will research the various conectors.

Bob
 
 