From a subpanel in the 2nd floor I ran an additional 12 Guage line with 15 Amp circuit breaker. The circuit breaker trips whenever two hair dryers are on at the same time. Can I replace the circuit breaker with a 20 Amp? Thanks for your advice.

Kevin
 
  #2  
Old 01-29-04, 12:05 PM
E
Member
Join Date: Apr 2001
Location: Cleveland, Ohio
Posts: 338
Received 0 Votes on 0 Posts
Technically yes, but two simultaneously operating hair dryers are likely to trip a 20A breaker as well.
 
  #3  
Old 01-29-04, 05:07 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,454
Received 0 Votes on 0 Posts
Agreed. Unless for some reason there is 14ga wire on the circuit, which there shouldn't be, there is no reason for this circuit to be on a 20 amp breaker.
 
 