50amp Extension


  #1  
Old 02-07-04, 09:20 AM
richmill20
Visiting Guest
Posts: n/a
50amp Extension

Can I use two wire cables containing 3-8 and 1-10 in parallel to make a 50 Amp extension cord of 25 ft in length? I would like to use this cable as it would be more flexable for my needs.
 
  #2  
Old 02-07-04, 04:13 PM
green jacket's Avatar
Member
Join Date: Sep 2000
Location: Williamsport and Blue Bell, Pennsylvania
Posts: 489
Upvotes: 0
Received 0 Upvotes on 0 Posts
I am interpreting your description to mean putting (3) #8 and (1) #10 wires together, with 50 amp cord caps at the ends.
Please clarify your objective.
If the interpretation I provided is the same as what you were saying, this is not an acceptable method. You really need a cord with the appropriate insulation, jacket, and amperage ratings.
The cord and connectors may need to be purchased at a supply house.

Please give more details, we may have additional suggestions to your application, that would be useful to you.

gj
 
  #3  
Old 02-07-04, 07:08 PM
richmill20
Visiting Guest
Posts: n/a
I have 50 feet of the 3-8 + 1-10 and want to double the wire and add 50A connectors. I would have 6-8 and 2-10 in this cable with like colors connected togeter to make a 25 foot 50 A extension. would this be safe to use?
 
  #4  
Old 02-08-04, 10:32 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 8,028
Received 513 Upvotes on 418 Posts
NO you can't do that. You are not allowed to parallel wires under 1/0 size.
 
 