heat pump neutral
#1
heat pump neutral
Perhaps someone could explain why all my 220v appliances require 2 load wires and a neutral and a ground but the heat pump compressor only has 2 load wires and a ground (that goes nowhere) and NO neutral, and works fine?
Thanks in advance.
Thanks in advance.
#3
If by all you mean your dryer & stove/range it is because they have 120 volt loads built into the unit. Such as a light bulb or timer. They are rated "120/240 volt"
Units such as; an a/c compressor, heat pump compressor, air compressor, big wall a/c, welder, water heater, all do not require a neutral since there are no 120 volt loads in the units. They are straight 220 (or240) volt.
Units such as; an a/c compressor, heat pump compressor, air compressor, big wall a/c, welder, water heater, all do not require a neutral since there are no 120 volt loads in the units. They are straight 220 (or240) volt.
#4
Yes I Think I
Can, most appliances need 220 and 110 to operate, therefore the need for a neutral, however the heat pump only needs 220 Volts so nho need for Neutral!!
Example Dryer , Heating coils run at 220 Volts while the motor usually is 110 Volts
Hopes this help clear it up!!!
Example Dryer , Heating coils run at 220 Volts while the motor usually is 110 Volts
Hopes this help clear it up!!!
#5
The only difference between a 120-volt circuit and a 240-volt circuit is the voltage. A circuit only needs two current-carrying conductors no matter what the voltage. The electrons flow in on one and out on the other. When you see three current-carrying conductors going to an appliance, it's because it's really two circuits, one providing 120 volts and one providing 240 volts. Jerry's and Pete's clothes dryer reference is a perfect example.
#6
heat pump neutral
Ok,
Let me see if I can paraphrase:
In a 120 appliance, the line side contributes 120 volts which alternate back & forth through the hot line and dead neutral.
In my 240 v heat pump, the 120v phase A line alternates back & forth across the 120v phase B line while the phase B side is doing the same thing which, in effect, is adding the 2 voltages together making 240 v total. If this is correct, I can deduce that if the 2 cables going to the heat pump each originated from the same line coming off the pole (both phase A for example), then I would have only 120 v power at the compressor which would have to complete the circuit through ground (with less than desired results, I'm sure). True?
So now my curiosity is up, can you recommend a link that might explain the mechanics, if you will, of 3 phase power?
Let me see if I can paraphrase:
In a 120 appliance, the line side contributes 120 volts which alternate back & forth through the hot line and dead neutral.
In my 240 v heat pump, the 120v phase A line alternates back & forth across the 120v phase B line while the phase B side is doing the same thing which, in effect, is adding the 2 voltages together making 240 v total. If this is correct, I can deduce that if the 2 cables going to the heat pump each originated from the same line coming off the pole (both phase A for example), then I would have only 120 v power at the compressor which would have to complete the circuit through ground (with less than desired results, I'm sure). True?
So now my curiosity is up, can you recommend a link that might explain the mechanics, if you will, of 3 phase power?
#8
"dead neutral"??? There's nothing dead about a neutral!
If each hot wire originated on the same line coming off the pole, then there would be no voltage at all between these two wires and you would have no source of 240 volts at the heat pump. If the heat pump had any 120-volt components (and I have no idea whether yours does or not), those would still work. But the 240-volt parts of your heat pump would be dead.
Current should never, ever flow on a grounding wire except in the case of a fault. None of the parts of an appliance that are supposed to conduct electricity are connected to the grounding wire. Unless something breaks, circuits are never completed through the grounding wire. Any time the grounding wire conducts electricity, the breaker should trip if the fault protection is working correctly. When there is a short at the appliance, the grounding wire conducts thousands of amps for thousanths of a second.
By the way, since we are speaking precisely, the term "ground wire" doesn't apply here. You don't have one at the heat pump. You have a "grounding wire" and maybe a "grounded wire" (aka neutral).
Before we move on to three-phase (which is many times more complicated), let's make sure you're clear on single-phase.
If each hot wire originated on the same line coming off the pole, then there would be no voltage at all between these two wires and you would have no source of 240 volts at the heat pump. If the heat pump had any 120-volt components (and I have no idea whether yours does or not), those would still work. But the 240-volt parts of your heat pump would be dead.
Current should never, ever flow on a grounding wire except in the case of a fault. None of the parts of an appliance that are supposed to conduct electricity are connected to the grounding wire. Unless something breaks, circuits are never completed through the grounding wire. Any time the grounding wire conducts electricity, the breaker should trip if the fault protection is working correctly. When there is a short at the appliance, the grounding wire conducts thousands of amps for thousanths of a second.
By the way, since we are speaking precisely, the term "ground wire" doesn't apply here. You don't have one at the heat pump. You have a "grounding wire" and maybe a "grounded wire" (aka neutral).
Before we move on to three-phase (which is many times more complicated), let's make sure you're clear on single-phase.