Gfci


  #1  
Old 02-24-04, 09:12 PM
I
Member
Thread Starter
Join Date: Feb 2004
Location: Texas
Posts: 24
Upvotes: 0
Received 0 Upvotes on 0 Posts
Gfci

My 120vac class A Group I GFCI turns itself off about 5 seconds after power is applied. Is that delay in turning itself off, a sign that the circuit breaker itself is bad rather than wiring shorts or opens etc?

My experience is an instantaneous tripping when there is a wiring or downstream device problem.
 
  #2  
Old 02-25-04, 08:20 AM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
Are you talking about a GFCI breaker, or a GFCI receptacle? Is the GFCI completely unloaded when you apply power, or is there a load? There is no 5-second delay in a GFCI, so something more is going on here.
 
  #3  
Old 02-26-04, 07:48 PM
I
Member
Thread Starter
Join Date: Feb 2004
Location: Texas
Posts: 24
Upvotes: 0
Received 0 Upvotes on 0 Posts
The GFCI that I am talking about is a circuit breaker. The only thing in the line are receptacles and light swithes.

When I switch on, it switches itself back off, but not immediately. I thought that might be a known symptom of bad circuit breaker.
 
  #4  
Old 02-26-04, 07:55 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
If the breaker is tripping after five seconds, then it's an overload trip, not a GFCI trip (or the breaker is bad). Do an experiment. Swap out the GFCI breaker and put in an equivalent non-GFCI breaker. See if it still trips. If not, buy a new GFCI breaker. If the non-GFCI breaker trips too, then hunt for the overload. It could be caused by a high-resistance short somewhere on the circuit. Could even be caused by a nail or screw used on new siding or to hang a picture or mount a bookshelf.
 
 