Stove Receptacles

What’s the difference between 3-wire and 4-wire female stove receptacles? Is one better than the other? And finally, can I use the same type of wire (i.e., 6 gauge, three insulated conductors plus ground) for connecting both types? Thanks—Marc
 
Sponsored Links
  #2  
Old 03-07-04, 09:12 PM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
3-wire uses one wire for both neutral and ground.
4-wire has separate wires for neutral and ground.
4-wire is better (i.e., safer), which is why it is required on all new installations (since 1996).
3-wire is still allowed in certain situations by a grandfathering clause in the NEC that recognizes that it's impractical to rewire every house built prior to 1996. 3-wire was introduced (for stoves and dryers) during WWII to save materials for the war. I guess that by 1996 they figured the war was over.

If you run a new cable with three insulated conductors plus a ground, then you must attach it to a 4-hole receptacle. If the current stove has a 3-prong cord and plug, then you also must convert it to a 4-prong cord and plug, separating the neutral wire from the chassis at the stove.
 