Receptacle Under The Kitchen Sink?
Old 03-23-04, 07:24 PM
MKM
MKM is offline
While looking at a new home purchase, we noticed the garbage disposal, rather than being hardwired, was plugged into a receptacle located in the cabinet under the kitchen sink ??! I was quite surprised to see this. It just didn't seem right. To make this worse, neither the circuit nor the outlet were GFCI protected. Is this a violation of code, or just bad common sense?
Thanks...
Old 03-23-04, 08:04 PM
hotarc
This is commonplace and perfectly acceptable, as long as your locality permits it. Often times the dishwasher and the disposal will share a duplex receptacle and one of the individual receptacles is connected to a switch above the sink to operate the disposal.
GFCI protection is not required because the receptacle is not readily accessible and the motor may cause nuisance trips.
Old 03-24-04, 10:24 AM
hornetd's Avatar
Disconnecting means
The cord and plug connection serves as the disconnecting means for the disposal. This allows for the replacement or servicing of the unit without disturbing the home's wiring. It is specifically permitted by the US NEC as quoted below.
Tom
422.16 Flexible Cords.
(A) General. Flexible cord shall be permitted (1) for the connection of appliances to facilitate their frequent interchange or to prevent the transmission of noise or vibration or (2) to facilitate the removal or disconnection of appliances that are fastened in place, where the fastening means and mechanical connections are specifically designed to permit ready removal for maintenance or repair and the appliance is intended or identified for flexible cord connection.
(B) Specific Appliances.
(1) Electrically Operated Kitchen Waste Disposers. Electrically operated kitchen waste disposers shall be permitted to be cord-and-plug connected with a flexible cord identified as suitable for the purpose in the installation instructions of the appliance manufacturer, where all of the following conditions are met.
(1) The flexible cord shall be terminated with a grounding type attachment plug.
Exception: A listed kitchen waste disposer distinctly marked to identify it as protected by a system of double insulation, or its equivalent, shall not be required to be terminated with a grounding-type attachment plug.
(2) The length of the cord shall not be less than 450 mm (18 in.) and not over 900 mm (36 in.).
(3) Receptacles shall be located to avoid physical damage to the flexible cord.
(4) The receptacle shall be accessible.
(2) Built-in Dishwashers and Trash Compactors. Built-in dishwashers and trash compactors shall be permitted to be cord-and-plug connected with a flexible cord identified as suitable for the purpose in the installation instructions of the appliance manufacturer where all of the following conditions are met.
(1) The flexible cord shall be terminated with a grounding-type attachment plug.
Exception: A listed dishwasher or trash compactor distinctly marked to identify it as protected by a system of double insulation, or its equivalent, shall not be required to be terminated with a grounding-type attachment plug.
(2) The length of the cord shall be 0.9 m to 1.2 m (3 ft to 4 ft) measured from the face of the attachment plug to the plane of the rear of the appliance.
(4) The receptacle shall be located in the space occupied by the appliance or adjacent thereto.
(5) The receptacle shall be accessible.