Wire splices in a panel/subpanel

I have a 100A subpanel in a shed which feed2 swimming pool equipment. The panel contains the main, a 2-pole 50A for the heater, a 2-pole 15A for the pool pump/chlorinator, and a 1-pole 15A GFI breaker for the required receptacle and pool light.

I want to add another 15A breaker to supply some lighting for the shed (in and out) as well as a couple more GFI receptacles.

When I opened the subpanel, I noticed that the pump and chlorinator wires are wire-nutted together and then connected to the breaker. Similarly the pool light is switched using a switch loop, and these connections are also wire-nutted inside the panel.

For some reason, I was under the impression that splices were not allowed within the panel, but I don't know where I got that impression.
 
Sponsored Links
  #2  
Old 03-31-04, 05:47 AM
HandyRon's Avatar
Member
Join Date: Dec 2001
Location: New York
Posts: 1,365
Received 0 Votes on 0 Posts
Splices are ok within your panel, as long as you don't pack them in.
From the electric code:
"The conductors, including splices and taps, shall not fill the gutter to more than 75% of its area."
 
  #3  
Old 03-31-04, 06:19 AM
BuzzHazzard
Visiting Guest
Posts: n/a
Thanks Ron. Pretty black and white.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: