Question GFCI or Split Receptacles in Kitchen??

I am planning on installing 2 receptacles about 18 inches from either side of my kitchen sink.

Do these receptacles need to be GFCI or split??
 
  #2  
Old 04-13-04, 07:09 AM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,245
Upvotes: 0
Received 0 Upvotes on 0 Posts
I don't understand the 'split' reference in the question. Countertop receptacles must be GFCI protected.
 
  #3  
Old 04-13-04, 07:16 AM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
In the U.S., GFCI.
In Canada, split.
Wherever you are, ???

Installing split receptacles with GFCI protection is possible but a pain in the neck, so split kitchen receptacles are not common in the U.S.

In Canada, split kitchen receptacles are required but GFCI is not.
 
 