Occasional Short Circuit
#1
Member
Thread Starter
Join Date: May 2004
Posts: 15
Upvotes: 0
Received 0 Upvotes
on
0 Posts

My basement bathroom is has a light and an exhaust fan which are fed through a GFCI. The light and fan are separately switched but are both powered from the load side of the GFCI. SOMETIMES, when the light and fan are both switched on and the fan is then switched off, the GFCI will trip. This doesn't happen every time, and never happens when only the fan is on and is then turned off. Do I have a short/How can I fix it?
Help - it's a dark room without windows!!
Help - it's a dark room without windows!!
#2
Shorts cannot be detected by GFCIs.GFCIs detect any imbalance in the current that travels between the hot & the neutral.Your GFCI is defective,sorry I didnt come right to the point,just needed to clarify.
#3
Replacing the GFCI might fix it. But it might not. Cheap bathroom exhaust fans, especially as they age, often have enough leakage in the windings to trip a GFCI. After trying the new GFCI, you could also try a better fan. But you might need to put the fan on the line side of the GFCI.
#4
Member
Thread Starter
Join Date: May 2004
Posts: 15
Upvotes: 0
Received 0 Upvotes
on
0 Posts

Thanks. Both the fan and GFI are new, but I have a spare GFI and will try it. What had puzzled me was that the GFCI only tripped at the instant the fan switch was turned off.