40 amp breaker for 30 amp central a/c


  #1  
Old 05-25-04, 10:18 AM
trindel
Visiting Guest
Posts: n/a
40 amp breaker for 30 amp central a/c

I own a home that was built in the mid 50s and has 100 amp service. I am adding a 3 ton central a/c unit that has a 30 amp requirement. The house used to have an electric stove, which was connected to a 40 amp breaker. Can I use this line to power the a/c unit or do I need to replace the 40 amp breaker with a 30 amp breaker?
 
  #2  
Old 05-25-04, 10:51 AM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,246
Upvotes: 0
Received 0 Upvotes on 0 Posts
No. And now I am padding my answer so that it will be accepted.
 
  #3  
Old 05-25-04, 11:20 AM
P
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 1,983
Upvotes: 0
Received 0 Upvotes on 0 Posts
"30 amp requirement"------ this could apply to two distinct ratings-- the rating of the Banch-Circuit breaker and the Branch-Circuit condutors.

If you have an existing 40-amp breaker, it MAY be connected to 40amp conductors--- #8 copper. To detemine the ampacity of the Branch-Circuit conductors needed, multiply the Full-Load current of the compressor-motor by125%.The NEC requires that full-load current-value be marked on the compressor-motor name-plate, the equiptment name-plate, or both. The FLC X 125% value may appear on the name-plate as "minimum circuit (conductor)ampacity-- 26 amps." This value requires #10 condutors.

To determine the rating of the Branch-Circuit breaker,multiply the FLC X 175%.The minimum rating of the C-B may appear on the name-plate. It's important to know that the rating of the C-B will exceed the rating of the B-C conductors---- ex.;A 40-amp C-B protecting 30 amp conductors.

Good Luck & Enjoy the Experience!!!
 
 