15 amp receptacles on 20 amp circuit?

I see most receptacles sold at home centers are the 15 amp/120 volt variety. And that's what I used when I replaced all my receptacles in my house. Now I found out some of those receptacles are on 20 amp circuits when I checked my service panel recently. Is this safe? I haven't had any problems. Should I go and replace all the receptacles on 20 amp circuits with 20 amp receptacles?
 
Sponsored Links
  #2  
Old 06-29-04, 06:18 AM
Member
Join Date: Dec 2000
Posts: 510
It is perfectly safe and legal to put 15A receptacles on a 20A circuit (as long as there is more than one receptacle on the circuit, which is almost always the case). The only difference between a 15A and a 20A receptacle is that the 20A can accept either 20A or 15A plugs. Since almost nothing used in a residential setting has a 20A plug (except maybe some air conditioners), there is little reason to ever use a 20A receptacle.
 
  #3  
Old 06-29-04, 06:21 AM
scott e.'s Avatar
Member
Join Date: Jun 2003
Location: Anderson, IN
Posts: 412
FYI, a duplex receptacle counts as two outlets on a circuit.
 
  #4  
Old 06-29-04, 06:24 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
You're in good company. 99% of all receptacles on residential 20-amp circuits are 15-amp receptacles.
 
  #5  
Old 06-29-04, 06:35 AM
txdiyguy's Avatar
Member
Join Date: Mar 2003
Location: Dallas, Texas
Posts: 249
Maybe even 99.9%
 