I have a new out building/shop that I need to run power to. The building is approx. 100 ft from my panel. I need enough power for lights and a power tool from time to time also keeping in mind future needs. My main panel is a 200 amp Square D home line that has plenty of room. Need Help !
 

Last edited by outbldg; 06-29-04 at 02:06 PM.
  #2  
Old 06-29-04, 12:37 PM
scott e.'s Avatar
Member
Join Date: Jun 2003
Location: Anderson, IN
Posts: 386
Upvotes: 0
Received 0 Upvotes on 0 Posts
I think that I can gleen a question in there somewhere. I think that you are asking for advice on what type of power to run to your building. At a minimum, I would put at least a 60A sub panel in the building. This could be even larger, depending on the types of loads you intend to use. (i.e. welders, big power tools, etc.)
 
  #3  
Old 06-29-04, 12:45 PM
outbldg
Visiting Guest
Posts: n/a
Exclamation

Yes I did omit the questions. In addition to the 60 amps that you recomended what about breaker size, wire size, conduit size or direct burial, and can this be done on a budget
 

Last edited by outbldg; 06-29-04 at 02:02 PM.
  #4  
Old 06-29-04, 02:07 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
There are several factors to consider:
  • How many square feet is the outbuilding?
  • Will the outbuilding ever require air conditioning or heat?
  • Will you ever use a kiln or large welder there?
  • What about a refrigerator or freezer?
  • Garage door opener?
  • Will any part of it ever be made into livable space?
A 60-amp subpanel can be done with 6/3 UF-B cable direct buried (i.e., no conduit) off a 60-amp breaker.

The bulk of the effort is the digging. So if you want to save money and you have a strong back, that's a good place to start. You can save more money doing the interior wiring of the outbuilding yourself. Then maybe you could just hire out the connections at both panels, and the grounding rod. If you have technical skills and are willing to study up, you could do the whole job yourself.

But don't skimp on the permit. Get a permit and have the work inspected.
 
 