Code Question

Is there a maximum number of ELs that can be used with Sched 80 PVC conduit (1 1/2 in) and #2 THHN Copper? My subpanel project needs a few 90 degree turns to get to a large enough knockout in the panel without tearing into the wall cavity completely.

Thanks

Leslie
 
  #2  
Old 07-13-04, 12:13 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
Can't have more than 360 degrees of bends between pulling points. Even so, you probably want to limit yourself to 270.
 
  #3  
Old 07-13-04, 12:13 PM
P
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 1,983
Upvotes: 0
Received 0 Upvotes on 0 Posts
Not to exceed the equivalent to four 90-degree bends.
 
  #4  
Old 07-13-04, 01:03 PM
L
Member
Thread Starter
Join Date: Jun 2004
Posts: 75
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by John Nelson
Can't have more than 360 degrees of bends between pulling points. Even so, you probably want to limit yourself to 270.
A pulling point being a place to grab wire and pull from. So is the removable cover type El is considered to be a pulling point?

Thanks

Leslie
 
  #5  
Old 07-13-04, 01:19 PM
M
mgb
mgb is offline
Member
Join Date: Jun 2004
Posts: 134
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes it is.
 
  #6  
Old 07-13-04, 01:37 PM
L
Member
Thread Starter
Join Date: Jun 2004
Posts: 75
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by mgb
Yes it is.

Perfect. Thanks for a quick response. It will make the project much easier to finish using those ELs.

Leslie
 
  #7  
Old 07-13-04, 01:44 PM
M
mgb
mgb is offline
Member
Join Date: Jun 2004
Posts: 134
Upvotes: 0
Received 0 Upvotes on 0 Posts
You're welcome. Good luck!
 
 