Ampacity rating on Romex

Is it safe to install romex 'in' insulation? IE taking two bats of fiberglass and sandwiching them around the wire which is 2 inches from the bottom of the joist. I see nothing in the NEC which would require derating th cable, but it seems taht heat would not be able to dissipate like it doe sin open air.

Thanks,
Matthew
 
Sponsored Links
  #2  
Old 07-19-04, 08:13 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Yes, it's safe. No additional derating is required for this condition.
 