Adding 50amp breaker to subpanel

Reply

  #1  
Old 07-23-04, 10:46 AM
workingonmyhome
Visiting Guest
Posts: n/a
Adding 50amp breaker to subpanel

I am running a new 220 line to a 50amp breaker for a range. An electrician is coming to do the hookup.

The main panel is full. It is outside. We have a subpanel in the house with space/rooom. Is there any problem with leaving the exising 30amp breaker and outlet (it won't be used and hidden by cabinets) and adding the 220/50amp breaker to the subpanel?
 
Sponsored Links
  #2  
Old 07-23-04, 11:00 AM
mgb
mgb is offline
Member
Join Date: Jun 2004
Posts: 136
No problem that I'm aware of but I would at least remove the wires from the shut off breaker and tape the ends. Also tag the wires as to what they fed so the future residents will know.
 
  #3  
Old 07-23-04, 01:05 PM
workingonmyhome
Visiting Guest
Posts: n/a
Thanks mgb for the quick response. It is good to have availability to smart folks.
 