Multi-wire circuit questions


  #1  
Old 07-23-04, 04:58 PM
Kray
Visiting Guest
Posts: n/a
Multi-wire circuit questions

Couple of questions about the requirement for double pole breaker and pigtailed neutrals:

1. Is a double pole breaker always required for a multiwire circuit? Could be wrong but I thought I saw a response awhile back that said that the requirement applies when the two hot wires run to the same device, but not when they do not. I have a multiwire circuit where the two hots power two separate outdoor circuits, and do not run to the same device. It currently has a double pole breaker and I have no reason to change it, but was just wondering if the requirement is "absolute."

2. Also, are pigtailed neutrals also always required for a multiwire circuit or are there any circumstances where they are not? In the circuit described above, I do have an "unpigtailed" neutral that I can fix if required.

Thanks
 
  #2  
Old 07-23-04, 05:20 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
Is a double pole breaker always required for a multiwire circuit?
It is sometimes, but not always, required. But it is always a good idea.

Could be wrong but I thought I saw a response awhile back that said that the requirement applies when the two hot wires run to the same device, but not when they do not
True. In technical jargon, substitute the word "yoke" for "device", since a duplex receptacle is really two devices on one yoke.

Also, are pigtailed neutrals also always required for a multiwire circuit or are there any circumstances where they are not? In the circuit described above, I do have an "unpigtailed" neutral that I can fix if required
Yes, pigtailed neutrals are always required when the neutral is serving two hots.
 
 