Install lighting 1000 feet away
I want to install lighting at my entrance gate, but it is 1000 ft. from my electrical source. I want pole lights, with 3 6o watt bulbs in each. Any ideas? Solar lighting doens't seem to be sufficient.
#2
1000 feet is very, very far to run 120-volt power, and very far to dig a trench. So every amp is costly. Exactly how many post lights are we talking about? For one post, use 12-gauge wire. For two, use 10-gauge. For three, use 8-gauge. For four, use 6-gauge. You can fudge on these numbers if you don't mind that the bulbs are dim and half your power is consumed by the wire.
You might decide that solar is better after all.
You might decide that solar is better after all.
#3
Member
Join Date: Dec 2000
Posts: 475
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Maybe one or more of these:
http://www.siliconsolar.com/portable_power_system.htm
combined with high-efficiency lighting (CFL or LED) might do the trick.
I cringe to think of the time/cost to bury 1000' of wire just for a few lights...
http://www.siliconsolar.com/portable_power_system.htm
combined with high-efficiency lighting (CFL or LED) might do the trick.
I cringe to think of the time/cost to bury 1000' of wire just for a few lights...
#5
Member
Join Date: Dec 2000
Posts: 475
Upvotes: 0
Received 0 Upvotes
on
0 Posts
You still need to dig 1000' feet of trench 18" deep. This is difficult and expensive. If you are OK with that then read on.
Running 240V with a shared neutral will cut your voltage drop by a factor of four if you put one pole light on each phase and the wattage of each pole light is the same. With 2 180W fixtures (1.5A each) the voltage drop with 12 gauge (1.6 ohms @ 1000') is 2.4V; with 14 gauge (2.5 ohms @ 1000') the voltage drop is 3.75V. Either value is OK for lighting, but don't plan on adding much more load to the circuit.
Running 240V with a shared neutral will cut your voltage drop by a factor of four if you put one pole light on each phase and the wattage of each pole light is the same. With 2 180W fixtures (1.5A each) the voltage drop with 12 gauge (1.6 ohms @ 1000') is 2.4V; with 14 gauge (2.5 ohms @ 1000') the voltage drop is 3.75V. Either value is OK for lighting, but don't plan on adding much more load to the circuit.
#7
Member
Join Date: Dec 2000
Posts: 475
Upvotes: 0
Received 0 Upvotes
on
0 Posts
John:
Think of it this way:
(1) Put both fixtures on a single circuit, producing a voltage drop of X volts split equally between the hot and the neutral.
(2) Now put each fixture on its own circuit with separate neutrals. Because the current is halved, the voltage drop is cut in half to X/2 volts, again split equally between hot and neutral (X/4 volts drop on hot, X/4 volts on neutral).
(3) Now share the neutrals. Since the loads are perfectly balanced, the currents in the shared neutral cancel - no current, no voltage drop. The only voltage drop is in the hot (X/4 volts).
Think of it this way:
(1) Put both fixtures on a single circuit, producing a voltage drop of X volts split equally between the hot and the neutral.
(2) Now put each fixture on its own circuit with separate neutrals. Because the current is halved, the voltage drop is cut in half to X/2 volts, again split equally between hot and neutral (X/4 volts drop on hot, X/4 volts on neutral).
(3) Now share the neutrals. Since the loads are perfectly balanced, the currents in the shared neutral cancel - no current, no voltage drop. The only voltage drop is in the hot (X/4 volts).