Half-hot receptacle

I have a half-hot receptacle that, bottom to switch, top on. I replaced it with a new one and now the switch doesn't work with either top or bottom. Seems like both,top and bottom, are now hot because the lamp will work if plugged into either. I assumed I wired it wrong. What should I check for? Electrical scares me...
 
Sponsored Links
  #2  
Old 09-09-04, 06:34 PM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Very common problem. Do you still have the old receptacle you took out? If so, very carefully compare the old receptacle with the new one. You'll notice that on the brass-screw side of the new receptacle, there is a tab that electrically joins the two screws. But on the old receptacle, that tab has been removed. So get a pair of pliers (with the breaker off of course) and bend that tab back and forth a couple of times until it breaks off. Do this on the brass-screw side only. There is a tab on the silver-screw side too, but leave it there.
 
  #3  
Old 09-10-04, 05:42 PM
Mojo702
Visiting Guest
Posts: n/a
Thank you...

That worked great!! Thanks. Is that something "insiders" know? I was never able to find any mention of that.
 
  #4  
Old 09-10-04, 07:24 PM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Mojo,

Where did you look to get your information? Any good electrical book would discuss duplex recepticles.
 