sub panel

A few years back I installed a 60 amp subpanel in my garage. The garage is 75 feet from the house. The wiring runs underground in PVC conduit. I had my electrical work inspected and it passed with no problem. I have been doing some reading and now wondering if I should have installed a separate grounding rod at the subpanel? If so why didn't the inspector pick it up. Any ideas of this?
 
Sponsored Links
  #2  
Old 09-19-04, 05:23 AM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
Received 0 Votes on 0 Posts
If an inspector didn't notice you had no ground rod at a detached structure he wasn't looking very well.
Yes, you should install one with #6cu to the panel. If you ran 3 feed conductors to the sub then you do NOT isolate the grounds and neutrals.
If you ran 4 conductors (hot,hot,neutral,ground) then you have to keep the grounds and neutral isolated in the sub. A separate ground bar in the panel may be necessary.
 