SER In PVC

I am running 200 feet of PVC out to a pole barn and thought it would be easier to pull a SER cable through the pipe rather than some 4-Single conductors. Is SER permitted in PVC since in some cases pvc is considered a wet location?? Thanks
 
Sponsored Links
  #2  
Old 09-27-04, 02:43 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
SER is not permitted underground, even in conduit. And pulling four individual conductors will be much easier than pulling SER.
 