Rigid metal conduit as defacto ground rod
Old 09-28-04, 05:50 PM
sandsmarc
I am doing a garage subpanel and was intending to install a ground rod. However, I ran my THWN conductors about 60 feet underground through rigid metal conduit. Can that act as my ground rod. It is buried 8 inches and runs for 60 feet.
Old 09-28-04, 05:59 PM
R
No. You must have a real ground rod.
Old 09-29-04, 08:44 AM
P
If the S-P is located in a structure which is seprate from the structure where the Service is located, you are required to have both an Equiptment Grounding Conductor between the two stuctures, and a Grounding Electrode (copper rod) at the detached structure.
The U-G RMC can serve as the EGC IF it forms a solid metallic path between both ends of the "run", and both ends should be "Bonded" to the metallic enclosures at each end.
I advise that at the S-P you fit a "Bonding-Bushing" on the end of the RMC inside the S-P, and connect a Bonding Jumper between the Bonding-Bushing and a Grounding terminal bar which is throughly Bonded to the metal surface of the enclosure.
The Equiptment Grounding Conductors of the Branch-Circuit, the Grounding Electrode Conductor to the Ground-rod, and the Bonding-Jumper all will connect to the Grounding terminal bar.
The ONLY connections to the Neutral terminal bar are the Feeder Neutral conductor,and the Neutral conductors of the Branch-Circuits.
Good Luck & Enjoy the Experience!!!!!!!!!!!
Old 09-30-04, 04:16 PM
Speedy Petey's Avatar
Actually you are only required to have an EGC if there are other metallic paths between the structure, such as a water pipe or phone/cable between the buildings.
The point is moot though since you are only 8" deep. 3/4" galv pipe can be used as a grounding electrode in lieu of a ground rod but it must be driven to "at or below grade" or it can be laid in a trench 30" deep.
I honestly cannot say if I think the conduit run itself can be the grounding electrode if it were 30" deep. I have never run across such a situation and never considered the scenario.