Double pole GFCI breaker
#1
Member
Thread Starter
Join Date: Oct 2004
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts

I am converting my pool to 220 volt and bought a double pole GFCI breaker. There are 2 load connections, a neutral connection and the pigtail which goes to ground. All I have at the pump is 3 wires-2 hots and a ground. Will the breaker work properly without a neutral connection between the breaker and the pump? This forum has been a big help to me so thanks to everyone who responds.
Steve
Steve
#2
If you have no 120-volt components, the neutral connection is unnecessary. Go ahead and connect the pigtail to the neutral bar (not the same thing as the grounding bar except in the main panel). but you will have no wire to connect to the third screw on the breaker. It will work just fine. The neutral connection exists because many pools have 120-volt components such as lights.