Amperage Issues with Jet Pump

I have a 1/3 hp jet pump which in the past ran on a 15 amp household circuit.
However, now if I plug it into a 15 amp circuit the fuse blows. But, if I plug it into a 20 amp circuit it runs fine.
Any ideas?
FB
 
Sponsored Links
  #2  
Old 11-21-04, 09:38 PM
nomind's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2004
Location: langley, in sunny fraser valley, bc , near vancouver
Posts: 1,133
Cool

Sounds like a lot of amps for a small motor. I don't recall any 1/3 pumps that take more than 8-9 amps. If possible try measuring the actual amps consumed by the motor, using a clamp-on ammeter at the pressure switch.
 
  #3  
Old 11-22-04, 07:15 AM
TomZ1's Avatar
Member
Join Date: Sep 2003
Location: New Hampshire
Posts: 174
Is this a 120V circuit?

I agree with Nomind...it seems like a lot of amps. I installed a 1/2 HP jet pump on 120V. It drew 9.4 amps. I later converted it to 240V (it's a dual voltage pump) and it now draws 4.7V.

Perhaps a loose connection?

Please explain the reference to "plugging in" the pump. Is it hardwired to the circuit?

It sounds like there are other things on the circuit which may draw enough amps to trip the breaker. Generally water pumps should have dedicated circuits.
 
  #4  
Old 11-22-04, 10:54 AM
Member
Join Date: Sep 2000
Location: Fayetteville, NY, USA
Posts: 1,052
Frank,

If it is a 120v circuit, a 1/3 HP motor draws 7.2 full-load amps (FLA). But NEC Article 430, Motors, requires that you multiply the FLA times 2.5 to size your breaker, or 1.75 times if you have fuses.

Hence, a breaker would have to be 20 amps, a fuse would have to be 15 amps. (7.2 amps * 1.75 = 12.6, so you'd go up to the next standard size fuse, or 15 amps.) In an ideal world, that fuse should not be blowing if only the motor is connected to that circuit.

My guess is either something else is on that circuit, or perhaps you have some wiring anomalies (loose connection, short circuit, etc.), or there is a problem with the pump.
 