Outdoor Knob & Tube


  #1  
Old 11-12-04, 02:28 PM
khg
Visiting Guest
Posts: n/a
Outdoor Knob & Tube

I just bought a 60 yr old house that has some knob & tube wiring running outside to a flood light. What type of wire is required for outside use (the current wire runs under the eave of the house and I would like to replace it in the same place)? Does the wiring have to be enclosed or can outdoor UL rated wire be attached directly under the eave? Thanks.
 
  #2  
Old 11-12-04, 03:02 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
If it is supported at least every 4.5 feet, not subject to sunlight (unless the cable is marked sunlight-resistant) and not in a location subject to physical damage (subjective call), then UF-B cable stapled to the eave is fine. All splices must be in permanently accessible junction boxes.
 
 