Ground wire hot to touch
I was in the basement turning off the water to the outside faucet when I noticed the pipe was warm. The ground wire from the service entrance panel is attached to the pipe. I touched where the wire is attached and it is HOT!
Also, all lights in house brighten and dim, especially when it is damp outside.
Lights also brighten or dim when furnace runs. Any help is appreciated. Could I have a loose ground?
Also, all lights in house brighten and dim, especially when it is damp outside.
Lights also brighten or dim when furnace runs. Any help is appreciated. Could I have a loose ground?
#2
Member
Join Date: Jan 2004
Location: Oregon
Posts: 1,104
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Turn off your main breaker and call your power company immediately!
You don't have a loose ground, you have a loose neutral wire on the power feed into your house. In fact, it sounds like the neutral is totally open. Electric current is returning to the transformer via your ground connection, possibly through the metal piping to your neighbor's houses.
Your symptoms are absolutely, totally clear. Get this fixed _now_.
-Jon
You don't have a loose ground, you have a loose neutral wire on the power feed into your house. In fact, it sounds like the neutral is totally open. Electric current is returning to the transformer via your ground connection, possibly through the metal piping to your neighbor's houses.
Your symptoms are absolutely, totally clear. Get this fixed _now_.
-Jon
#4
Member
Thread Starter
Join Date: Nov 2004
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks to both of you! It hasn't done it for a couple days now...it has been like this off and on for over a year. I thought it was a problem with the city's electrical since they have 10 houses running off this same pole. When it gets light tomorrow, I want to look in my SEP and tighten things down if needed.
If that does not help with the warm pipe, I will call power Co. Thanks!