breaker size, wire guage, circuit spec


  #1  
Old 12-26-04, 07:58 PM
BloodSweatTears
Visiting Guest
Posts: n/a
Talking breaker size, wire guage, circuit spec

Hi,

I am wondering if theer is a FAQ aroudn to explain how to pick a breaker size and wire gauge, as well as design a circuit for 2 220V heaters for my basement.

One is 2kW and the other is 1.5kW. Can I put them on the same wire and breaker (the easiest for me)?

What is the guideline or equation for figuring the number of amps that a breaker should be rated for. The ding-ding working at Home Depot must've had a rough Christmas because he didn't seem to know!

Any help appreciated, but explanation preferred. Thanks....

B
 
  #2  
Old 12-26-04, 08:16 PM
BloodSweatTears
Visiting Guest
Posts: n/a
Hello out there guys, I know you are here...

Please help me out with an answer to your good buddy up here in Canada

B
 
  #3  
Old 12-26-04, 09:45 PM
A
Member
Join Date: Mar 2000
Location: Lake Murray, SC USA
Posts: 1,413
Upvotes: 0
Received 1 Upvote on 1 Post
BST - Welcome to the DIY Forums.

I am a Chemical Engineer, not an Electrical Engineer, but here is my take:

If my memory serves me correctly, Volts X Amps = Watts

So, Amps = Watts/Volts or for your case, 2000 Watts/220 Volts = 9.09 Amps

and, 1500 Watts/220 Volts = 6.82 Amps

So, it would appear a 20 Amp Breaker should do it. And that should mean 12 gauge copper wire.

I am not an expert in this field, just offering my take on this.
 
  #4  
Old 12-26-04, 10:07 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
The manufacturer of the heating equipment should provide installation instructions, and you should (must) follow their advice.

If the manufacturer provides no guidance, arkayassoc's analysis is correct.
 
  #5  
Old 12-27-04, 06:51 AM
T
Member
Join Date: May 2001
Location: Dry Side of Washington State
Posts: 685
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by arkayassoc
I am a Chemical Engineer, not an Electrical Engineer, but here is my take:

If my memory serves me correctly, Volts X Amps = Watts

So, Amps = Watts/Volts or for your case, 2000 Watts/220 Volts = 9.09 Amps

and, 1500 Watts/220 Volts = 6.82 Amps

So, it would appear a 20 Amp Breaker should do it. And that should mean 12 gauge copper wire.
3500 Watts/240 Volts = 15 Amps X 1.25% = 18 amps (this is the formula for the U.S. NEC).
 
  #6  
Old 12-27-04, 09:43 AM
J
Member
Join Date: Sep 2000
Location: Fayetteville, NY, USA
Posts: 969
Upvotes: 0
Received 2 Upvotes on 2 Posts
The logic behind Thinman's reply: NEC doesn't want you to connect more than 80% of the rating of a circuit's wire or breaker. Multiplying connected amps x 1.25 keeps you at 80%.

Juice
 
 