pool light tripping breaker?

Reply

  #1  
Old 12-27-04, 07:19 AM
ged
Visiting Guest
Posts: n/a
Lightbulb pool light tripping breaker?

I have a Sta-Rite 500W pool light that is controlled by a Intermatic timer. When the light is switched off it trips the breaker. The breaker does not trip when the light is on, only when it is off. Any ideas? I am assuming that the light fixture needs to be replaced but I am not sure. Thanks.
 
Sponsored Links
  #2  
Old 12-27-04, 09:21 AM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 5,599
Sounds like an improperly wired switch loop. The breaker is actually tripping when you turn the switch on. Tell us how the wires are connected at the light and the switch.
 
  #3  
Old 12-27-04, 09:45 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
ged, some history would improve our guesses. Did this work perfectly for years and then one day just fail, with no changes? Or did somebody change something? Or did the origin of the problem coincide with some event?
 
  #4  
Old 12-27-04, 04:42 PM
Member
Join Date: Dec 2004
Location: So. Calif.
Posts: 540
could be several things, but leave the breaker that supplies current to the light off untill it is fixed . for your safety.


steve
 
  #5  
Old 01-10-05, 07:55 AM
ged
Visiting Guest
Posts: n/a
Smile

I turned off the power, pulled the light out of the niche and it was half full of water, so I drained the water out and re-adjusted the gasket and it has worked fine ever since then. Of course this was the day after I was the winning bidder of a new light fixture on ebay. Thanks for the suggestions and advice!
 