ser vs seu
#1
ser vs seu
I am looking to use it to install a 100AMP subpanel in my basement.
What is the difference between SER and SEU cable? I have been looking for SER #4 Copper in my area...but I can only find SEU in the lower guages.
I am assuming SEU does not have a ground...if this is the case...can a seperate ground be used?
Thanks for the help
What is the difference between SER and SEU cable? I have been looking for SER #4 Copper in my area...but I can only find SEU in the lower guages.
I am assuming SEU does not have a ground...if this is the case...can a seperate ground be used?
Thanks for the help
#2
SEU is serivce cable used to connect a residence to the utility power.It has 2 hot conductors & 1 neutral.SER is used to connect a sub-panel to the main panel feeding it {like in your case}. Code requires that the grounds & neutrals from branch circuits in a sub-panel be seaparated on different busbars.Therefore SER contains 2 hots, an insulated neutral & a ground.Do you have access to Al {aluminum} SER cable? Although it has less ampacity, as long as the connections are done properly it works just as well as Cu {copper} cable.A seaparate ground cannot be used per the NEC,all circuit conductors must be run in the same conduit or cable assembly.