High and Low Voltage run together
Can regular house circuits, catv, and tel wire run in the same space?
Depends on exactly what you mean by "space". Yes if you mean a stud cavity. No if you mean a junction box.
Even if allowed by code, it's usually a bad idea to have line voltage close to low voltage for interference reasons. Somewhere between one and two feet of separation is good. And it's usually not a problem if they cross at right angles or are together for only a very short distance (an inch or two). It depends on what kinds of signals are running on the low-voltage wire and how well shielded the low-voltage wire is.
Also, you can't run low voltage and high voltage circuits in the same raceway, such as power (120/240) and thermostat (24V). Along with what John said, code says that all the conductors in a raceway shall be insulated to the highest voltage present.
Don't quote me on that; it is just something from memory. I think I'm right, though