  #1  
Old 01-08-05, 07:54 PM
pb4021
Visiting Guest
Posts: n/a
need to add a 240 line.

I have a 200amp panel with plenty of open slots.
I would like to add a line with 240 service..
its a ge panal so i went and picked up a ge breaker 40 amp double pole.
my question is this..
it has a leg on each side of the breaker..(i assume thats 120 each side)
and that makes it 240.
so if I pick up 8/3 wire, one wire goes to each leg on the breaker and the 3rd goes to the ground bar? that makes it a 240 line?
 
  #2  
Old 01-08-05, 08:04 PM
R
Member
Join Date: Aug 2004
Location: NA
Posts: 962
Upvotes: 0
Received 2 Upvotes on 2 Posts
If by 8/3 you mean two conductor and a ground then yes. The 3 normally determines the number of conductors not counting the ground. So if this is only 240 volt and no 120 volt is needed you would technically need an 8/2 cable. What is it that you are running the the #8 cable to? You have the right idea on the breaker but make sure the wire that connects to the neutral/ground bar is bare or green the other two connect to the breaker it doesnt matter which leg goes where.
 
  #3  
Old 01-09-05, 11:44 PM
pb4021
Visiting Guest
Posts: n/a
thanks for the reply..
the 8/3 is running to a sauna but thanks for clearing that up..lol
I just wish I saw it before I went and returned the 8/3 and bought 12/3
I looked on the sauna panal and saw that it listed 12ga. min in wire so...
I guess I will be heading back to get 12/2, unless 10/2 would serve some better purpos
thanks
 
  #4  
Old 01-10-05, 12:52 AM
G
Member
Join Date: Oct 2004
Location: USA
Posts: 676
Upvotes: 0
Received 0 Upvotes on 0 Posts
This is getting scary.
You can NOT put 12 ga wire rated for 20 amps on a 40 amp breaker.
There may be special grounding requirements for a sauna.
For safety you need to get an electrician.
 
  #5  
Old 01-10-05, 01:54 AM
pb4021
Visiting Guest
Posts: n/a
very nice of you, thanks

might just do that..


just wondering though...
if the sauna has it listed right on the panel 12ga. min wire and it only has 3 poles 2hot and one ground.
what could be the special part?
aside from the $$$$$$?

12ga wire and 20 amp double pole breaker sounds scary?
 
  #6  
Old 01-10-05, 02:33 AM
J
Member
Join Date: Nov 2004
Location: West Palm Beach, Florida
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts

There should be a nameplate on the sauna somewhere, (motor, or controller) with the minimum and maximum circuit ampacity and breaker sizing.

#12 wire for 20A, #10 for 30A and #8 for 40A.
 
  #7  
Old 01-10-05, 06:50 AM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
Okay, are we talking about a 40-amp breaker or a 20-amp breaker? You seem to have said it both ways.
 
  #8  
Old 01-10-05, 05:37 PM
pb4021
Visiting Guest
Posts: n/a
Originally Posted by John Nelson
Okay, are we talking about a 40-amp breaker or a 20-amp breaker? You seem to have said it both ways.
sorry, guess I was not clear in my posts
I first bought 8-3 and a 40amp double pole breaker.
I was getting ready to start my adventure and after taking the sauna out of the box I saw the plate that was mentioned above ( by jerry)
sooo, once I saw the 12ga. min wire listed on the plate, I went back and returned the items I had.
exchanging them for 12-3 and a double pole 20amp breaker...
and once again it looks like I will be going back to get 12-2, since I only need 2 hots and 1 ground.
hope that clears my post up a little.
 
  #9  
Old 01-10-05, 05:43 PM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,245
Upvotes: 0
Received 0 Upvotes on 0 Posts
There are a myriad of code requirements for a sauna. Not sure what you have exactly, but you need to comply with all the code requirements. This is not a time to guess.
 
 