NEMA 5-20P Convert to NEMA 5-15P

I have a device I am wanting to use which will work with a 15 or 20 amp circuit. However all I have are NEMA 5-15P plugs and the device has NEMA 5-20P plugs. Are there converters out there to change these plugs? Something similar to going from a three prong to a two prong?

Thanks for your help all!
 
Sponsored Links
  #2  
Old 01-11-05, 10:22 AM
Member
Join Date: Sep 2000
Location: Fayetteville, NY, USA
Posts: 1,052
Received 1 Vote on 1 Post
I believe what you mean is that you have all 5-15R receptacles. (The R is for receptacle, the P is for plug.) Any device that has a 5-20P plug is to be used only on a 20 amp circuit. Any device with that plug style should not be used on a 15 amp circuit. That's why they are required to provide the 5-20P plug. Also, no receptacle connected to a 15 amp breaker or fuse should be a 5-20R. I would determine which 20 amp circuit or circuits in my home I would use this device on and change the receptacle nearest where it would be used to a 5-20R. You probably know this but I'll mention it - a 5-20R receptacle will accomodate either standard 5-15P and 5-20P plugs.

Juice.
 
  #3  
Old 01-11-05, 10:40 AM
akant
Visiting Guest
Posts: n/a
Juice,

You are correct I have 5-15R's in my home but for some reason the breakers which connect to these circuits are rated at 20amp. So I was wondering if given my setup if I could use a a converter of sort to convert the 5-20P to work with a 5-15R or could I just replace the 5-15R with a 5-20R. If I have the correct 20amp circuit and not the correct recpticle can I still replace it even if there may other other 5-15R's hangling off the circuit?
 
  #4  
Old 01-11-05, 11:11 AM
ampz's Avatar
Member
Join Date: Feb 2004
Location: Philadelphia
Posts: 536
Received 0 Votes on 0 Posts
There are no converters to allow a 20a cord end to be plugged into a 15a receptacle. The 5-20p is on the deivce you have because of its higher amp draw. Juice is right, if you can change a receptacle on one of the 20a circuits to a 5-20R receptacle.You'll want to choose a circuit that has the fewest loads on it to avoid tripping the breaker.You must be certain it is a 20a circuit as installing a 20a receptacle on a 15a circuit is a code violation.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: