Pass through Amps on standard receptacle

Was looking at a bad GFCI I was returning to Home Depot today and notice it said both 20A on the GFCI load and 20A pass through current, which is what you'd expect of course. So I was wondering on your standard .50 15A receptacle, is the pass through current rated at 15A as well or will it handle 20A pass-through on 12/2 to a 20A circuit breaker? Or do I need to swap out several breakers?
 
Sponsored Links
  #2  
Old 01-12-05, 04:26 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
All 15 amp receptacles can handle a pass through current of 20 amps.
 
  #3  
Old 01-12-05, 05:46 AM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
Consider the fact that the device is a duplex. So in actuality it is two 15 amp receptacles. This is why just one duplex 15 amp device is allowed on a 20 amp circuit.
 
  #4  
Old 01-12-05, 08:37 AM
jhughe90
Visiting Guest
Posts: n/a
Mr

Originally Posted by racraft
All 15 amp receptacles can handle a pass through current of 20 amps.
That's what I had thought, thanks for the confirmation!
 