Hello we have romex run in all diff directions most not anchored. Iam splitting a ckt. for load safety. Added up things running. Question is what are a few good rules of thumb about romex running over the top of each other and next to each other . Thanks WP
 
Sponsored Links
  #2  
Old 01-22-05, 05:03 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Crossing at right angles (or close to right angles) is not an issue. You do have a problem with cable running parallel. Cables that run parallel for any length of time need to be derated. This means that a larger diameter cable is needed to safely carry the same current.
 
  #3  
Old 01-22-05, 06:44 AM
Member
Thread Starter
Join Date: Dec 2004
Location: USA
Posts: 34
Got it Thank you Oh do have a fair understanding of derating. WP
 