Hello I have a hot tub currenty wired and garage is currently wired.
My garage is separate located at the back of my property it is wired with, outdoor 8/3 in conduit which runs to just inside my house (36 feet). Inside the house 8/3 romex to the panel (30 feet) 30amp breaker at the garage and 30 amp breaker at the panel.
Hot tub is just off the back of our house 6/3 outdoor in conduit to 60amp GFCI at on the wall (10 feet) then 6/3 romex to panel (30 feet) with 60 amp breaker at panel.
I want to relocate the Hot tub next to the garage. the added length of wire would be approx another say 20 feet.
As the tub requires a 60A breaker and the panel in the garage is rated at 100A and main panel in the house is 100A. Can I use 6/3 for the run from the main panel to the garage or do I need to go for a larger size wire because of the length. Further is there a wire that I can pul through singley like service wire that is rated for below ground in conduit?
I can't get a straight answer and seem confused about this. My thoughts are because of the run length use 4/3
Any input is greatly appreciated
My garage is separate located at the back of my property it is wired with, outdoor 8/3 in conduit which runs to just inside my house (36 feet). Inside the house 8/3 romex to the panel (30 feet) 30amp breaker at the garage and 30 amp breaker at the panel.
Hot tub is just off the back of our house 6/3 outdoor in conduit to 60amp GFCI at on the wall (10 feet) then 6/3 romex to panel (30 feet) with 60 amp breaker at panel.
I want to relocate the Hot tub next to the garage. the added length of wire would be approx another say 20 feet.
As the tub requires a 60A breaker and the panel in the garage is rated at 100A and main panel in the house is 100A. Can I use 6/3 for the run from the main panel to the garage or do I need to go for a larger size wire because of the length. Further is there a wire that I can pul through singley like service wire that is rated for below ground in conduit?
I can't get a straight answer and seem confused about this. My thoughts are because of the run length use 4/3
Any input is greatly appreciated
#2
The conduit would have to be quite large (2"?) to fit #6 cable legally. Also it is quite frowned upon to run cable in conduit.
I would do it right and run conductors in the conduit.
Do not be concerned with the length. Maybe if you said 130' instead of 30' it would be a concern. The concern is that the tub will max out the circuit so nothing in the garage can be used while the tub is on full blast.
I would run #4 and use a 70 or 80 amp breaker. This may be taxing your 100 amp service though. But if you were not having a problem before you'll be OK, you're not actually adding anything.
I would do it right and run conductors in the conduit.
Do not be concerned with the length. Maybe if you said 130' instead of 30' it would be a concern. The concern is that the tub will max out the circuit so nothing in the garage can be used while the tub is on full blast.
I would run #4 and use a 70 or 80 amp breaker. This may be taxing your 100 amp service though. But if you were not having a problem before you'll be OK, you're not actually adding anything.
#3
Member
Thread Starter
Join Date: Aug 2004
Location: Toronto, Ontario
Posts: 87
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks Speedy, I am currently using a sqaaure D 100A subpanel in the garage it has space for 6 breakers. it is now supplied by using a 30A breaker in reverse to power the garage. Only think I have in there is a 220V compressor and lighting.
I am thinking like you said to place a higher capacity breaker with correct wiring of coarse. and although the house has 100A service I would never be at or near 100A. So I am assuming that I will be ok???
Also you said to use conductors which ones are legal to run in conduit? and when I get inside the house I stil go back to the 4/3 cable then?
I am thinking like you said to place a higher capacity breaker with correct wiring of coarse. and although the house has 100A service I would never be at or near 100A. So I am assuming that I will be ok???
Also you said to use conductors which ones are legal to run in conduit? and when I get inside the house I stil go back to the 4/3 cable then?
#5
Member
Thread Starter
Join Date: Aug 2004
Location: Toronto, Ontario
Posts: 87
Upvotes: 0
Received 0 Upvotes
on
0 Posts
uninsulated? I guess that means not in a jacket like NM6/3 would be?
So I would use 3.....4 guage conductors and a ground conductor?
Would size ground conductor would I require? would 8/3 suffice
So I would use 3.....4 guage conductors and a ground conductor?
Would size ground conductor would I require? would 8/3 suffice
#7
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,246
Upvotes: 0
Received 0 Upvotes
on
0 Posts
What Speedy is saying is that once your circuit leaves the house, you must have an insulated ground wire. This applies to pools and spas. You cannot run an uninsulated ground wire outside the house for these circuits.
You are correct, your NM 6/3 is no good outside the house.
You are correct, your NM 6/3 is no good outside the house.
#8
Member
Thread Starter
Join Date: Aug 2004
Location: Toronto, Ontario
Posts: 87
Upvotes: 0
Received 0 Upvotes
on
0 Posts
ahh ok insulated gorund. got it.
Runing 4/3 in a 1 1/2" conduit is going to be almost impossible. What type of wire can I run in the conduit that is rated for outside in a single wire format by which i mean not 4 wires together in a casing
Can sirvice entrance wire be used? Also wires of this guage would be difficult to attach with marrets. Is there a better way? Sorry for all the questions but I want to do this the right way even if it is overkill.
Runing 4/3 in a 1 1/2" conduit is going to be almost impossible. What type of wire can I run in the conduit that is rated for outside in a single wire format by which i mean not 4 wires together in a casing
Can sirvice entrance wire be used? Also wires of this guage would be difficult to attach with marrets. Is there a better way? Sorry for all the questions but I want to do this the right way even if it is overkill.
#9
Don't think interms of 4/3. You need; 3- #4THWN & 1- #6THWN green. The green can possibly be #8 but many tubs require #6 min so I would be safe.
Don't forget you need a ground rod at the sub-panel since it is a detached structure. Are you up on all the other codes involved with sub-panels and spa feeds?
Don't forget you need a ground rod at the sub-panel since it is a detached structure. Are you up on all the other codes involved with sub-panels and spa feeds?