Replacing Existing Sub-Panel??
Old 02-08-05, 07:15 PM
bdek
I want to remove an older residential (8) fuse type sub-panel and replace it with one that has circuit breakers. The existing BX branch circuit cabling will connect to the new panel knockouts -- but the individual wires are not quite long enough to attach to the new breakers or the neutral bus. Can I splice additional wiring to the existing circuits in the new circuit breaker sub-panel (with wire nuts) so that I can reach each breaker and the neutral bus??
Thanks,
Bob
Old 02-08-05, 08:57 PM
No, but you can screw a box or two nearby and splice in there.
Old 02-08-05, 10:56 PM
I would have answered the question yes.
Old 02-08-05, 11:54 PM
NEC states you can as long as the splice is terminated on a breaker in that panel and that the panel is not used as a junction box to splice a circuit through.
Old 02-09-05, 01:26 AM
My mistake. But though the code allows that, would you do it?
I guess if you ...um, think someone might... work on the live panel you can't allow that kind of clutter.
Old 02-09-05, 07:16 AM
A few...maybe. A lot...no.
Old 02-09-05, 09:11 PM
bdek
Thanks very much guys for the quick response to my question. Appreciate the guidance and comments. I'm only going to do a few splices inside the new sub-panel so as to minimize the clutter. It' doable.
Thanks again,
Bob