Electrical Problem - Need help


  #1  
Old 02-21-05, 03:38 PM
henryr
Visiting Guest
Posts: n/a
Electrical Problem - Need help

hello all, i need some help.

i removed an outlet to install a GFI. there are two wires (2 black/2 white) and a ground. well both blacks are hot.... i thought one should be the line and the other the load. how do i wire up the GFI? just nut up the unused wire?? thanx
 
  #2  
Old 02-21-05, 03:46 PM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,246
Upvotes: 0
Received 0 Upvotes on 0 Posts
It is extremely unlikely that both black wires are hot wires. Only in a very strange (and incorrect) situation would this be the case.

How did you determine that both black wires were hot?

One other question. Is your intent to provide pass through protection to something else on this circuit? If so, what other device or receptacle did you want to provide pass through protection to?

If you did not want to provide pass through protection to something else, then it makes no difference which wires are line and which wires are load.
 
  #3  
Old 02-21-05, 03:55 PM
henryr
Visiting Guest
Posts: n/a
thanx for the reply. i tested both blacks with my electrical tester and the light comes on for both.

there is nothing down line that needs protection, so can i nut up one of the wires and just use the remaining?
 
  #4  
Old 02-21-05, 04:08 PM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,246
Upvotes: 0
Received 0 Upvotes on 0 Posts
No, you cannot put a wire nut on one of the wires. If you do so you will eventually find that something else in your house doesn't work.

Both wires are not hot. Your testing method is wrong.

How are you testing for power?

What are you using? A light bulb tester? A tick tester? Do you have all four wires completely disconnected when you test? What is your method?
 
  #5  
Old 02-21-05, 04:14 PM
henryr
Visiting Guest
Posts: n/a
the power is on. the four wires are sticking out of the electrical box spread apart from each other.

i am using a light bulb tester. a little test light.

i am getting "hot" for testing both blacks against the whites and both blacks against the ground wire.
 
  #6  
Old 02-21-05, 04:17 PM
G
Member
Join Date: Oct 2004
Location: Orlando, FL
Posts: 121
Upvotes: 0
Received 0 Upvotes on 0 Posts
Are both of these wires connected to the same circuit breaker? Did the old receptacle have the tab broken on the side with the gold screws? Either you have a duplex on two seperate circuits or someone ran a redundant wire.
 

Last edited by Garou; 02-21-05 at 04:19 PM. Reason: Typo
  #7  
Old 02-21-05, 04:56 PM
henryr
Visiting Guest
Posts: n/a
Originally Posted by Garou
Are both of these wires connected to the same circuit breaker? Did the old receptacle have the tab broken on the side with the gold screws? Either you have a duplex on two seperate circuits or someone ran a redundant wire.
ahhhh. yup, the top wires are on one circuit breaker and the bottom are on another breaker. what to do? pick one and nut the others up?

i couldn't tell anything by the outlet that i removed.

thanx
 
  #8  
Old 02-21-05, 05:06 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,262
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by henryr
i couldn't tell anything by the outlet that i removed.
Is this in the kitchen and are you in Canada?

If yes to both you cannot replace this receptacle with a GFI. You must use a two pole GFI breaker.
 
  #9  
Old 02-21-05, 05:41 PM
henryr
Visiting Guest
Posts: n/a
Originally Posted by Speedy Petey
Is this in the kitchen and are you in Canada?

If yes to both you cannot replace this receptacle with a GFI. You must use a two pole GFI breaker.

no, this is in the bath and i am in Atl, GA, USA.
 
  #10  
Old 02-21-05, 05:48 PM
G
Member
Join Date: Oct 2004
Location: Orlando, FL
Posts: 121
Upvotes: 0
Received 0 Upvotes on 0 Posts
Unless you are using a ton of appliances in your bathroom it would probably be alright to cap off a set of the wires and use the other for your GFI. The alternative is to change the breakers to GFI breakers and replace the receptacle you took out. Or replace the existing box with a 2-gang old work box, and install 2 GFI receptacles.
 
  #11  
Old 02-21-05, 06:16 PM
henryr
Visiting Guest
Posts: n/a
thanx for all the help.....
 
 