15 amp 2 pole,20 amp 2 pole

What are the disadvantages with the 15amp & 20amp 2 pole murray breakers. I ran out of slots on my 150amp service panel. Can I still run 10 recptacles on a 20amp 2 pole. Will either of these 2 poles trip more often? Are there any limitations on either the 15amp or 20amp 2 pole breakers?
 
Sponsored Links
  #2  
Old 02-25-05, 05:26 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
For a residential system in the US there is no limit to the number of receptacles or lights on a circuit. Forget that 10 rule, as it is not a rule. Receptacles and lights do not increase the load on a circuit, only plugging something in *and using it) and/or turning on the light increase the load.

Tandem breakers give you two breakers in the space of one. If you use a 20 amp tandem breaker then you can run two 20 amp circuits from it, instead of the one that you can run from a single 20 amp breaker.

The only limitations on tandem breakers are that the panel must support them.
 
  #3  
Old 02-28-05, 10:53 AM
Member
Join Date: Sep 2000
Location: Fayetteville, NY, USA
Posts: 1,052
Received 1 Vote on 1 Post
"The only limitations on tandem breakers are that the panel must support them." That is to say, they must be listed for use in your specific panel model.

Juice
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: