50 amp sub-panel

How many 20amp circuits can be safely run off a sub-panel supplied from a main panel’s 50amp breaker? The sub-panel will be supplying 4 or 5 basement lights a couple of outlets, a washing machine, a basement half bath, an island dishwasher, garbage disposal, compact microwave and warming drawer in a kitchen remodel, and another 20 amp circuit for a future upstairs bath. Will this be overloading this 50amp circuit?
 
  #2  
Old 02-28-05, 01:48 PM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,246
Upvotes: 0
Received 0 Upvotes on 0 Posts
You can run as many circuits as you want, up to what the sub-panel will allow, space wise.

What is important is what you want to have on thoise circuits turned on at the same time.
 
  #3  
Old 02-28-05, 01:54 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
How many 20amp circuits can be safely run off a sub-panel supplied from a main panel’s 50amp breaker?
42.

Will this be overloading this 50amp circuit?
Ah, much better question than your first question. A 50-amp 240-volt subpanel supplies up to 12KW of power. Let's do a ballpark calculation using conservative numbers:
  • 0.5 KW for the lights.
  • 1.0 KW for the two receptacles.
  • 1.0 KW for washing machine.
  • 2.0 KW for the basement half-bath.
  • 1.5 KW for the dishwasher.
  • 1.0 KW for the disposal.
  • 1.5 KW for the microwave.
  • 1.5 KW for the warming drawer.
  • 2.0 KW for the future bathroom.
You probably couldn't overload this is your turned on everything at once (which is so unlikely as to be not worth considering). Bottom line: you're okay.
 
 