GFI Breaker vs. Outlet

Whirlpool tub installation: why would it be a required to have a GFI BREAKER vs. a GFI outlet for the pump motor of a whirlpool tub ?
I would like to have an OUTLET instead so there is more convenience in RESETTING it at a location of my choice vs. the breaker box located in the basement.
Is there a code requirement for using a GFI breaker for this application ?
 
Sponsored Links
  #2  
Old 02-28-05, 05:10 PM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Who says you need the GFCI breaker? I see no reason why a GFCI receptacle (or dead front) wouldn't be better. Are you reading the Whirlpool installation instructions? If so, can you quote them to us?
 
  #3  
Old 02-28-05, 05:11 PM
Member
Join Date: Oct 2004
Location: Orlando, FL
Posts: 132
What I do when I wire a jetted tub on a new house, is run a home-run from the panel to a box facing a closet that borders the tub if there is one. From there I jump to a box near the motor in the access area. At trim I put a faceless (no slots for plugs) GFI in the closet and a 20-amp single receptacle by the motor.

If you don't have a place to put the faceless GFI, you should probably use a GFI breaker. However I've gotten away with putting 15 amp GFIs in the access areas (still on a dedicated 20 amp circuit though).
 