50 amp receptical

Reply

  #1  
Old 03-04-05, 03:30 PM
Hjudge49
Visiting Guest
Posts: n/a
50 amp receptical

I am installing a 50 amp receptical to power a motor home. I am planning to use 8 3G wire, and have recieved the receptical itself, but it has no wiring diagram. Anyone know where the ground and neutral wires go? This is a 4 prong receptical with a "d" shaped ground (I assume ) prong at the top and the other three at 3, 6 and 9 o'clock.
 
Sponsored Links
  #2  
Old 03-04-05, 03:48 PM
hornetd's Avatar
Member
Join Date: Aug 2001
Location: Maryland
Posts: 695
The terminals are coded.

The green screw gets the ground. The silver is for the neutral. The two brass screws get the red and black. Some receptacles may be marked with words or abbreviations instead.

The D or U shaped pin is indead the ground. The opposite pin is the neutral and the two in between them are the hots.
--
Tom H
 
  #3  
Old 03-04-05, 03:49 PM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
The two hots will go left and right, to the connections marked "X" and "Y". The neutral will go to the remaining non-grounding connection, marked "W". The ground of course goes to the connection marked "G".
 
  #4  
Old 03-04-05, 03:53 PM
hornetd's Avatar
Member
Join Date: Aug 2001
Location: Maryland
Posts: 695
Bang bang you shot me down.

Damm. Shaded by John Nelson again. I have to be quicker on the keyboard.
--
Tom H
 
  #5  
Old 03-04-05, 04:00 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,537
If it's a 50A 220V receptacle, the ground (d-shaped) should be at 12:00, the neutral (white wire) should be at 6:00, and the red and black hot wires should be at 3:00 and 9:00. Also, all of the slots should be vertical on a 50A. I'm not sure if #8 is large enough for 50A, someone else care to verify?
 
  #6  
Old 03-04-05, 05:37 PM
hornetd's Avatar
Member
Join Date: Aug 2001
Location: Maryland
Posts: 695
#8 Copper is OK

If that #8 is copper than it is fine for fifty amperes. If it is in the form of THHN or cable with XHHW conductors. If you run the circuit as non metallic cable; that most of us call by the trade name Romex; than you will have to use #6 AWG wire because in type NM #8 is limited to forty Amperes.
--
Tom H
 