AC Disconnect Height?

Is there a minimum height for the outdoor disconnect for my central AC unit?
The old unit was wired in directly, and I had the whole HVAC system replace recently, but the HVAC contractor didn't do the electrical. I'm going to add that myself.

Just wondered, though, about height off the ground. Seems as I drive around town and observe, they vary.
 
  #2  
Old 03-09-05, 09:34 AM
J
Member
Join Date: Sep 2000
Location: Fayetteville, NY, USA
Posts: 969
Upvotes: 0
Received 2 Upvotes on 2 Posts
I believe the rule is 6'-0" to the top of any electrical control. Switch handle applies. I would personally interpret this to mean when the handle is in the uppermost position it is no greater than 6-feet AFF (above finished floor).

Juice

Juice
 
  #3  
Old 03-09-05, 09:50 AM
C
Member
Thread Starter
Join Date: Jan 2005
Location: Missouri
Posts: 127
Upvotes: 0
Received 1 Upvote on 1 Post
Minimum, NOT maximum

It sounds as though your answer is saying the MAX that it can be. I'm asking does it have to be a MINIMUM above the appliance, grass, etc.

I'm not trying to put it right at ground level or anything - that's only common sense - but I didn't know if it had to be at so many inches or something.

Just like outlets are usually placed about 12" from floor, switches at 48", etc.

Didn't know if there was either a code or rule of thumb for where to place the disconnect.
 
  #4  
Old 03-09-05, 10:04 AM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
As far as I know, there's no minimum height for anything--not this, not outlets, not switches.
 
  #5  
Old 03-09-05, 10:08 AM
J
Member
Join Date: Sep 2000
Location: Fayetteville, NY, USA
Posts: 969
Upvotes: 0
Received 2 Upvotes on 2 Posts
I misunderstood, and went for maximum. The NEC actually says (in Article 220.24) that when the disconnect handle is in its highest position, the center of the grip must be 2 meters AFF, or 6'-7". It does not specify a minumum height. Rule of thumb? I'd go no lower than 48", personally, but that's instinct, and not Code.

Juice
 
  #6  
Old 03-09-05, 03:23 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,262
Upvotes: 0
Received 0 Upvotes on 0 Posts
For outside a/c condensors I typically install them so the top is about even with the top of the a/c unit. This puts them @ about 24"-36".
They are rain tight so it matters not if they get covered by snow.
 
  #7  
Old 03-10-05, 06:02 AM
C
Member
Thread Starter
Join Date: Jan 2005
Location: Missouri
Posts: 127
Upvotes: 0
Received 1 Upvote on 1 Post
Thanks for the replies and info. I'll proceed and probably put the box near the top of the unit also.
 
 