Improperly terminated 240V wire

I just found the old oven wire (50amp 120/240 volt 6 guage) stuffed up under the kitchen floor. We currently have a gas range. The breaker was on and the wire was terminated using only electrical tape. Too bad the inspector missed that! I assume it has been there for years. Is it up to code to terminate the wires in a metal electrical box that can handle the 6 guage wire using wire nuts at the end of the wires? This is my first time dealing with a 240 volt wire. I did shut off the breaker for the wire and I taped it so no one will accidently turn it on.

Thanks in advance
 
Sponsored Links
  #2  
Old 03-18-05, 07:32 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Yes, put wire nuts on the ends of the wire. But high-quality electrical tape is also a good insulator. So it's possible that what you have now is already okay. But leave the breaker off.
 
  #3  
Old 03-18-05, 10:07 AM
Member
Join Date: Sep 2000
Location: Fayetteville, NY, USA
Posts: 1,052
I would install #6 wire nuts and also tape them on. I would mark the junction box so a future owner will know what it is. Perhaps I would put red tape over the breaker once it is turned off to warn others not to turn it on. Make sure the junction box has a proper cover. These things being done, it is safe and to Code. (Although I don't believe Code requires the tape on the breaker, it just seems like a good idea to me.)

Juice
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes