Would like to convert two prong outlet which I believe is 110 to a three prong outlet to accomodate a space heater. What does the change entail? Thanks
 
Sponsored Links
  #2  
Old 03-18-05, 11:17 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,335
I think best way to do what you want to do is to replace the 2 prong receptacle with a 3-prong GFCI receptacle (~$13). A 2 prong is ungrounded, and it would take a lot of work rewiring the circuit with grounded cable for a proper 3 prong outlet. A GFCI receptacle provides shock protection without needing a ground wire.
 
  #3  
Old 03-21-05, 04:50 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
You may or may not be able to simply install a three prong receptacle. Your wiring MAY include a ground, or it may NOT include a ground. To properly install a three prong receptacle you either need a grounded circuit, or you need GFCI protection.

Note that installing GFCI protection will not cause the circuit to be grounded. However, a properly connected GFCI receptacle will provide a safe means of using appliances that require a grounded circuit.

To determine if your circuit is grounded means visually examining the wiring at the receptacle and at the panel and also using a tester or analog voltmeter to check the circuit.
 