Sub Panel Feeder

Can someone tell me what size conductors and conduit I need to feed a 100 amp sub panel? The run is about 40 feet.
 
Sponsored Links
  #2  
Old 03-23-05, 07:24 PM
ampz's Avatar
Member
Join Date: Feb 2004
Location: Philadelphia
Posts: 536
If you use copper #3 & if you use aluminum #2
 
  #3  
Old 03-24-05, 05:15 AM
Member
Thread Starter
Join Date: Feb 2005
Location: USA
Posts: 339
Sub Panel Feeder

If I use individual #3 copper with 2 hot 1 neutral and 1 ground what size conduit should I use?
 
  #4  
Old 03-24-05, 08:50 AM
Member
Join Date: Aug 2004
Location: NA
Posts: 1,065
What type conduit? If your using sch. 40 pvc conduit then 1 1/4 would be my choice allowing plenty of bending space and good sized LB's and other fittings. You can put 6 #3 awg in 1 1/4 sch. 40 pvc. The equipment ground wire does not need to be #3 awg it can be #8 awg copper.
 

Last edited by Roger; 03-24-05 at 09:37 AM.
  #5  
Old 03-25-05, 05:11 AM
Member
Thread Starter
Join Date: Feb 2005
Location: USA
Posts: 339
Sub Panel Feeder

I just learned that I can't use PVC conduit because it isn't allowed by the city code. Also, 60 amp is all I need so I am running #6 3-conductor with ground Romex.
 
  #6  
Old 03-27-05, 12:17 PM
ampz's Avatar
Member
Join Date: Feb 2004
Location: Philadelphia
Posts: 536
Running the RX in pipe is not allowed by NEC { if thats what you intended}.Is this to be run outdoors? If so UF or metal conduit is required
 