hey guys, got some wonderful info from the hvac section and thought I would check you guys out. I added a light fixture and switch In a new basement, when I swipe the swithc with the probe ( the one that beeps and glows red) about an inch or two away it reacts what did I do wrong?
 
Sponsored Links
  #2  
Old 03-31-05, 11:27 AM
yahoo_ 20002
Visiting Guest
Posts: n/a
bumb

maybe I did not sound right, I installed a switch and light from a recepticle feed. the recepticle, switch and light work, but when I test the switch in the on position with the probe it reacts, when I turn the switch off and swipe the probe it only reacts fro0m the hot side. Is this normal
 
  #3  
Old 03-31-05, 12:15 PM
yahoo_ 20002
Visiting Guest
Posts: n/a
bump

somebody helppppppp!!!!!!!!! Please
 
  #4  
Old 03-31-05, 12:31 PM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
What probe are you talking aboput?
 
  #5  
Old 03-31-05, 12:42 PM
yahoo_ 20002
Visiting Guest
Posts: n/a
Thanks for replying. the tester that looks like a pen and glows red and beeps when there is current. When I hold it away from the switch about two inches it reacts. I don't think this should happen
 
  #6  
Old 03-31-05, 01:08 PM
Member
Join Date: Mar 2005
Location: Central Florida
Posts: 149
You may have a tester designed to trace wiring behind walls, in which case the 2" range sounds reasonable. Check the instructions. They should explain if this is the case.
 
  #7  
Old 03-31-05, 01:22 PM
Member
Join Date: Nov 2004
Location: Sacramento
Posts: 89
I think you are fine. My guess is that you are off of a main circuit and therefore the black is always hot, but the white is not because it only has current (returning form the fixture) when the swith is on. I am not an expert though, so wait until you hear from someone who is - I am sure someone will weigh in today.
 
  #8  
Old 03-31-05, 02:40 PM
GregH's Avatar
Super Moderator
Join Date: Jan 2001
Location: Manitoba
Posts: 9,674
yahoo_ 20002,

What you have is a non-contact voltage probe.
They are very sensitive and only really to be used as a guideline when testing for power because they will often react to stray voltage.

This tool is really not to meant to be used for what you are doing.
I use these for troubleshooting but you need a lot of experience to sort out the bad readings and they are never to be used as a test before touching the wires.
You need a normal contact type voltage tester
 
  #9  
Old 03-31-05, 04:03 PM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 5,599
You readings sound correct to me. There is always live power in the switch box unless you turn off the breaker.
 
  #10  
Old 04-01-05, 04:46 AM
yahoo_ 20002
Visiting Guest
Posts: n/a
thanks, thats a big relief. Yeah the probe/ tester is one of those 5 buck gadgets that you use to get an idea with . and again thanks for all the replies
 