My book says that I put:
- six 12 gauge wires
or
- five 10 gauge wires
... in 1/2" metal conduit. The guy at Home Depot said I'm not allowed to put *any* 10-gauge wires inside of 1/2" conduit.
Who is right?
-Antun
Old 04-05-05, 07:10 PM
R
Received 2 Upvotes on 2 Posts
Antun, it actually depends on the type of wire and how it is insulated. the most common wire in conduit for residential purposes is thhn/thwn. This desigantion will be printed on the outside cover of the wire. Assuming you are using thhn/thwn you can put 9 conductors that are #12 awg or 6 conductors that are #10 awg in 1/2" rigid metal conduit. If you are using a different type wire then these numbers will likely change. You must also derate the ampacity for more than 3 current carrying conductors in a conduit/raceway.
Old 04-05-05, 08:23 PM
Speedy Petey's Avatar
What book told you this if I may ask?
Roger answered your question well but I will just make two comments.
Derating starts at 3 current carrying conductors, but we derate from the 90 deg C column. So for #14, #12 & #10 you need over 9 cc conductors to make a difference. Under 9 the amperages stay the same, even though you are derating. If that makes ANY sense at all.
Second, NEVER listen to a home center employee!!!! Your life may depend on it someday!
Old 04-05-05, 08:31 PM
Pendragon's Avatar
My book says:
TW, #12 = 7 conductors
THW, #12 = 4 conductors
THWN, #12 = 10 conductors
Can you even get 10, 12 gauge conductors to fit into a half inch piece of pipe?
Old 04-05-05, 09:09 PM
A
The Black & Decker Complete Guide to home wiring. It does mention the THHN/THWN designation, but I assumed that's what I had.
-Antun
Old 04-05-05, 09:12 PM
A
So here's what I want to do:
- Put three 10-gauge wires in there (there are already three of them there; I plan to remove & replace these).
- Add an additional two 12-gauge wires in.
So I will have 8 wires in total. It sounds like I'm OK there.
Thanks,
Antun
Old 04-05-05, 09:19 PM
R
Antun, I would say that black and decker is talking about EMT (electrical metallic tubing) this would explain the 5 # 10's but it would appear they have a misprint on the #12's. this would be 9 whether EMT or RMC conduit. They also might have meant 12 #14 awg in 1/2" EMT.
Old 04-05-05, 09:31 PM
Pendragon's Avatar
Here's a handy calculator I found...
http://www.electrician.com/calculato...alculator.html
Old 04-05-05, 09:32 PM
A
Thanks Roger
I take it that means I can put three 10s and two 12s in there?
-Antun
Old 04-05-05, 09:36 PM
R