My cold air returns to the furnace are in the floor joist bays. When running NM through joists, can I go through a cold air return?
 
Sponsored Links
  #2  
Old 04-15-05, 08:24 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Yes, if you are talking about the short way through, perpendicular to the air flow. Caulk around the holes.
 
  #3  
Old 04-15-05, 08:41 AM
Member
Join Date: Nov 2002
Location: SC
Posts: 171
Does the cable need to be protected or be plenum rated??
 
  #4  
Old 04-15-05, 09:37 AM
ElectricalMan's Avatar
Member
Join Date: Feb 2005
Location: Harrisonburg
Posts: 744
John,

Can you point me to the code on that one. I have heard of people doing it but I never have as I usually don't see the need..anyway it would have to maintain the fire rating of the item breached....BUT with that said....

Check out Art 300-22(b) in regards to ducts used for Environmental Air.
 
  #5  
Old 04-15-05, 11:54 AM
Member
Thread Starter
Join Date: Feb 2005
Location: USA
Posts: 339
Originally Posted by ElectricalMan
Can you point me to the code on that one. I have heard of people doing it but I never have as I usually don't see the need..anyway it would have to maintain the fire rating of the item breached...
My wire run will be perpendicular to the joists and the cold air return. How do you make the run from one side to the other without going through the cold air return?
 
  #6  
Old 04-15-05, 12:00 PM
Member
Join Date: Nov 2002
Location: SC
Posts: 171
Question. Is this enclosed metal ducting installed within the joists or is the space between the joists being used as an air handling purpose?
 
  #7  
Old 04-15-05, 12:47 PM
Member
Thread Starter
Join Date: Feb 2005
Location: USA
Posts: 339
To form the cold air return the HVAC guys fasten sheet metal to the bottom of two adjacent joists to close off a joist bay...so you have the subfloor above, a joist on each side and sheet metal across the bottom to create the plenum. This has been very typical construction here for years.

I notice 300-22(b) has an exception that allows running through a plenum for dwellings if the run is perpendicular to the plenum...that is if I understand the exception correctly. Can someone confirm this?
 
  #8  
Old 04-15-05, 12:52 PM
Member
Join Date: Nov 2002
Location: SC
Posts: 171
I think that's the exception John was refering to. It still is in 300.22 (C). in the 2005 code and looks kosher to me.
 