Running NM
#1
Member
Thread Starter
Join Date: Feb 2005
Location: USA
Posts: 336
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Running NM
My cold air returns to the furnace are in the floor joist bays. When running NM through joists, can I go through a cold air return?
#4
John,
Can you point me to the code on that one. I have heard of people doing it but I never have as I usually don't see the need..anyway it would have to maintain the fire rating of the item breached....BUT with that said....
Check out Art 300-22(b) in regards to ducts used for Environmental Air.
Can you point me to the code on that one. I have heard of people doing it but I never have as I usually don't see the need..anyway it would have to maintain the fire rating of the item breached....BUT with that said....
Check out Art 300-22(b) in regards to ducts used for Environmental Air.
#5
Member
Thread Starter
Join Date: Feb 2005
Location: USA
Posts: 336
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Originally Posted by ElectricalMan
Can you point me to the code on that one. I have heard of people doing it but I never have as I usually don't see the need..anyway it would have to maintain the fire rating of the item breached...
#7
Member
Thread Starter
Join Date: Feb 2005
Location: USA
Posts: 336
Upvotes: 0
Received 0 Upvotes
on
0 Posts
To form the cold air return the HVAC guys fasten sheet metal to the bottom of two adjacent joists to close off a joist bay...so you have the subfloor above, a joist on each side and sheet metal across the bottom to create the plenum. This has been very typical construction here for years.
I notice 300-22(b) has an exception that allows running through a plenum for dwellings if the run is perpendicular to the plenum...that is if I understand the exception correctly. Can someone confirm this?
I notice 300-22(b) has an exception that allows running through a plenum for dwellings if the run is perpendicular to the plenum...that is if I understand the exception correctly. Can someone confirm this?